Old building using 2/3 armor jacketed no ground conductor to feed apt panels. Of the four apts three have separate main breakers in the equipment room. So that makes those 3 panels inside the apts sub panels. Therefore a bonding jumper from the feeder jacket to the panel box will not work and these three panels would need to have there main feeders replaced with a cable that will have a grounded conductor. The other panel has cable from meter into its main breaker and bonded at that point. That panel is not a sub panel. Am I understanding this right ? You can not just make your own grounded conductor in a sub panel it needs to be carried from the main breaker location. Thus making the main feeders into the 3 apts not up to code.