"apparent" premature ballast failuredue to rooftop solar installation

Status
Not open for further replies.

craff

Member
So we have a building with many (25+) exterior HID flood fixtures. Over the last year our maintenance dept. has replaced 18 of the ballast, three to four times. building owner thinks it's the rooftop solar array inverters. I haven't been out to the jobsite yet. I'm thinking it might just be lamps with worng orientation or heat???? Any help????
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Why does the building owner think it is related to solar arrays? Do the exterior HID's burn during the day? Are you sure you are having to work on the same fixtures?
Correct voltage hook up to the ballast or mismatched lamps and ballast, or fixtures coming to an end of their service life come to mind way before blaming the solar.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I would definitely verify that the correct lamps were installed in the fixtures. I have replaced many a ballast where a maintenance person had installed the wrong lamp and destroyed the ballast.

Chris
 

iwire

Moderator
Staff member
Location
Massachusetts
I would definitely verify that the correct lamps were installed in the fixtures. I have replaced many a ballast where a maintenance person had installed the wrong lamp and destroyed the ballast.

I always check lamps against ballasts, far too often they are replaced with any lamp that fits.

PAR 20 39 Watt Metal halides get replaced with the far cheaper PAR 20 incandescent lamps all the time in retail stores.
 