210.51(C)(5) says the receptacle(s) in the appliance garage are not considered as the required outlets. Seems like that would mean they can't be on the small appliance circuit. But they are in my house and I would think that they always should be. Is there some way to say the appliance garage receptacles must be on the small appliance circuit? Then how about other receptacles that are excluded, like more than 20" above the counter intended for an appliance above the countertop?
What got me thinking about this is someone had a small countertop removed to install a range in that location and wanted the countertop receptacle moved up to be in the cabinet to serve a micro-hood. Seems like that shouldn't be allowed.
Second question, did the 1989 code not require two SA circuits for the counter tops? This house built in 92 only had one. The island countertop extended slightly more than 6" where the receptacle was, but I found 1993 code didn't yet have that rule.
What got me thinking about this is someone had a small countertop removed to install a range in that location and wanted the countertop receptacle moved up to be in the cabinet to serve a micro-hood. Seems like that shouldn't be allowed.
Second question, did the 1989 code not require two SA circuits for the counter tops? This house built in 92 only had one. The island countertop extended slightly more than 6" where the receptacle was, but I found 1993 code didn't yet have that rule.