I purchased the 2005 Electrical NEC Exam Preparation review book from the Mike Holt site. While reading it, I found something in CH6 that does not seem correct, or at least I do not understand it.
The confusion is concerning the application of 110.14 (c). It may be easier to ask the question in the form of an example.
If for example, I am trying to size a conductor for a 50 Amp load where, I do not know the terminal temperature rating and I would like to use THHN.
110.14(c) tells me that, because I do not know the terminal temperature rating, I must use the 60deg C column of 310.16 therefore, I need #6AWG with a capacity of 55Amps. This I understand.
If I need to consider ambient temperature, because I expect it to be in excess of 30 deg C, then I would apply the correction factor in the table below 310.16 based on the column for THHN. For example ambient temp of 100 deg F would be a 0.91 correction factor. This I understand.
If I need to have more than 3 current carrying conductors in a conduit, I need to consider the correction factor in 310.15(B)(2)(a). For example 4 current carrying conductors would be a correction factor of 0.80. This too, I understand.
Now, what if I put all of this together, what would the correct size be?
70*.91*.80=50.96 Amps, meaning I must use a #4AWG
Or
75*.91*.80=54.6 Amps, meaning I must use a # 6AWG.
You see the difference?
In the first solution I am using the rule of 110.14(C) and applying the correction factors to the capacity in the 60 deg C column.
In the second I am applying the correction factor to the capacity in the 90 deg C (THHN) column.
It would appear based on the examples in CH6 that when I do not need to consider anything other than terminal temperature ratings, I should use the 60 deg C column. But as soon as I need to consider anything else, I should use the column associated with the insulation type.
Which is correct?
Or
Which is correct?