I purchased the 2005 Electrical NEC Exam Preparation review book from the Mike Holt site. While reading it, I found something in CH6 that does not seem correct, or at least I do not understand it.
The confusion is concerning the application of 110.14 (c). It may be easier to ask the question in the form of an example.
If for example, I am trying to size a conductor for a 50 Amp load where, I do not know the terminal temperature rating and I would like to use THHN.
110.14(c) tells me that, because I do not know the terminal temperature rating, I must use the 60deg C column of 310.16 therefore, I need #6AWG with a capacity of 55Amps. This I understand.
If I need to consider ambient temperature, because I expect it to be in excess of 30 deg C, then I would apply the correction factor in the table below 310.16 based on the column for THHN. For example ambient temp of 100 deg F would be a 0.91 correction factor. This I understand.
If I need to have more than 3 current carrying conductors in a conduit, I need to consider the correction factor in 310.15(B)(2)(a). For example 4 current carrying conductors would be a correction factor of 0.80. This too, I understand.
Now, what if I put all of this together, what would the correct size be?
70*.91*.80=50.96 Amps, meaning I must use a #4AWG
Or
75*.91*.80=54.6 Amps, meaning I must use a # 6AWG.
You see the difference?
In the first solution I am using the rule of 110.14(C) and applying the correction factors to the capacity in the 60 deg C column.
In the second I am applying the correction factor to the capacity in the 90 deg C (THHN) column.
It would appear based on the examples in CH6 that when I do not need to consider anything other than terminal temperature ratings, I should use the 60 deg C column. But as soon as I need to consider anything else, I should use the column associated with the insulation type.
Which is correct?
The confusion is concerning the application of 110.14 (c). It may be easier to ask the question in the form of an example.
If for example, I am trying to size a conductor for a 50 Amp load where, I do not know the terminal temperature rating and I would like to use THHN.
110.14(c) tells me that, because I do not know the terminal temperature rating, I must use the 60deg C column of 310.16 therefore, I need #6AWG with a capacity of 55Amps. This I understand.
If I need to consider ambient temperature, because I expect it to be in excess of 30 deg C, then I would apply the correction factor in the table below 310.16 based on the column for THHN. For example ambient temp of 100 deg F would be a 0.91 correction factor. This I understand.
If I need to have more than 3 current carrying conductors in a conduit, I need to consider the correction factor in 310.15(B)(2)(a). For example 4 current carrying conductors would be a correction factor of 0.80. This too, I understand.
Now, what if I put all of this together, what would the correct size be?
70*.91*.80=50.96 Amps, meaning I must use a #4AWG
Or
75*.91*.80=54.6 Amps, meaning I must use a # 6AWG.
You see the difference?
In the first solution I am using the rule of 110.14(C) and applying the correction factors to the capacity in the 60 deg C column.
In the second I am applying the correction factor to the capacity in the 90 deg C (THHN) column.
It would appear based on the examples in CH6 that when I do not need to consider anything other than terminal temperature ratings, I should use the 60 deg C column. But as soon as I need to consider anything else, I should use the column associated with the insulation type.
Which is correct?