When supplying power to multiple 208V fan coil units with an RLA of 1.5 amps, 2.5 amps, etc., does each FCU require individual short circuit & ground fault protection (i.e. fused at 15 amps in each local disconnect)? Or can a single 15A circuit breaker provide power to multiple FCU's without needing individual SCGF protection at the unit (local disconnect only)?
Applying 430.53(A) Not Over 1 Horsepower, I don't see any guidance on how many fan coil units you can connect in a single 15A circuit. 430.53(B) indicates that the branch circuit will not open. But I don't see this mentioned as a bullet point in 430.53(A). Am I missing something?
Applying 430.53(A) Not Over 1 Horsepower, I don't see any guidance on how many fan coil units you can connect in a single 15A circuit. 430.53(B) indicates that the branch circuit will not open. But I don't see this mentioned as a bullet point in 430.53(A). Am I missing something?