What difference does the breaker size in the subpanel make as long as the breaker feeding it protects the wires going to that subpanel?Originally posted by wnut4:
Electrican installed a 225 amp service for a house,also installed a 200 amp main breaker sub panel upstairs fed with 4/0 al SER cable from a 125 amp breaker located in 225a main panel,should this be allowed since sub has 200a main brk. or should sub have been MLO panel.
For long runs you are often forced to run larger sizes of wire than you might for shorter sizes anyway so I suspect CB terminals allow you to up size at least a couple wire sizes.Originally posted by izak:
some manufactures actually consider that electricians might want to run something larger than the Minimum