Say I have a six-plex apartment building. What is the minimum size feeder I am allowed to serve the individual dwelling units with?
Say I have a six-plex apartment building. What is the minimum size feeder I am allowed to serve the individual dwelling units with?
You have not listed enough information to give a qualified answer.
PJholguin![]()
This may be affected by the local code applicable to apartments or other rentals which may require a larger feed then the NEC.
Tapatalk!
What else do you need?
IMO 100 amps based on 225.39(C). I know others will say that that is only for the disconnect but I disagree
While I would agree with you I think we need to think about 225.39(D) "All Others. For all other installations, the feeder orbranch-circuit disconnecting means shall have a rating of not less than 60 amperes"
IMO, The minimum would be based on your 220 load calculations.
To meet the requirement for a dwelling unit it would have a bath and provisions for cooking so I would think 2 kitchen and 1 bath circuit. Depending on the square footage, you might even get by with a 30 amp 240/120 feeder.
I have heard those arguments but how do we reconcile 225.39. ...
To qualify under Article 225, the entire feeder must be outside or originate in another building.Dennis: I guess someone. ...
Article 230 concerns services, not feeders.In my view a 6 unit apartment building would require a minimum of a 60 amp feeder based on 230.79 or larger if Art. 220 calcs showed otherwise.
Article 230 concerns services, not feeders.
The NEC doesn't do "good." It only does "safe." So my answer is that we don't have to reconcile it. It requires a minimum disconnect size, but it would allow a smaller feeder size. I could install a 60 or 100 amp rated fused disconnect, then install 30 amp fuses and a feeder rated for only 30 amps, and not violate 225.39.. . . how do we reconcile 225.39? . . . The article is about the disconnect size but what good is that if the feeder isn't sized accordingly?
My only excuse is it's early here and the brain is not fully up to speed.
I was thinking of individual services. But then obviously it would then not be a multifamily dwelling, rather a one family dwelling and would need 100 amps anyway.
Better put my thinking cap on before I respond further.
I don't think 225 applies here either.To qualify under Article 225, the entire feeder must be outside or originate in another building.
I assume George is talking about a feeder within the complex...
FWIW, Article 215 only mentions the word dwelling in 215.2(A)(4) which basically says a dwelling unit feeder is not required to be larger than service conductors.