I don't think 225 applies here either.
Interesting that you mention 215.2(A)(4). While not relevant to this discussion, I just noticed it has a typo. It refers you to 310.15(B)(6), it should be (7). (6) was correct in the 2008 code.
Also, 215.2(A)(4) has been removed in the 2014 NEC.
I find it curious that 310.15(B)(7) refers to ALL dwelling units. That seems to imply that 100 amp would be the minimum, but I don't see anything else in the code that says there is any minimum size feeder for an individual dwelling unit in a multifamily building.
310.15(B)(7) is nothing more than an alternate method of selecting conductor ampacity if certain criteria is met and has nothing to do with determining minimum ampacity required.