Regarding 210.12 (B), is a dining room a formal dining room only or is an area off the kitchen where a table may be placed also a dining room? Arc Fault requirements are coming here on Jan 1 and as far as I can see, that would be the only required area where a 20A AFCI would be needed. In the past, I would just put an area where the table would go on one of the SABC's but they don't need AFCI protection.
 
is a dining room a formal dining room only or is an area off the kitchen where a table may be placed also a dining room?

IMHO both are dining rooms and as such both need AFCI protection.

Chris
 
So I guess I could just put one of the SABC's on an arc fault breaker and feed the dining room that way. I was just going to put the DR on a separate 20A circuit but in some of my houses, the dining room may only contain a couple of receptacles and that seems like overkill to run an AFCI circuit for that. I assume there is no conflict putting a GFI recept on an arc fault breaker?
 
There is no conflict with AFCI and GFCI.

I would run a separate circuit for the dining area and breakfast nook (if you will) and be done wiith it-- no GFCI but AFCI is needed. Of course you still need your 2 SABC on the counter.
 
Agreed but actually there is no reason why the DR recepts couldn't be on the load side of a GFCI recept.....

I agree, there is no reason that the Dining room receptacles can't be supplied from the load side of a GFCI. In fact I see this from time to time in new homes in my area.

Chris
 
I have not tried it but I have been told by ec's that the GFCI and Arc Fault don't play well together.
Interesting, I have never had a problem with AFCI and GFCI. I must admit I have not had the two together since the combo AFCI's came out but they should not be an issue. Everyone I have talked too has had no problem.
 