Actually smoke detector and carbon monoxide detector all in one is hard wired. No outlet.
Actually smoke detector and carbon monoxide detector all in one is hard wired. No outlet.
Actually smoke detector and carbon monoxide detector all in one is hard wired. No outlet.
Outlet. A point on the wiring system at which current is taken to supply utilization equipment.
We've even debated whether a switch box is considered to be an outlet.As packersparky stated it still is an outlet by Article 100 definition. It does not have to be a receptacle to be an outlet.
The box is not the outlet. The outlet may be within the box. If all that is in the box is a simple switch, there is no outlet, that switch does not fit the NEC definition of outlet.We've even debated whether a switch box is considered to be an outlet.
I have combo smoke detrctor and carbon monoxide detector hard wired. Not sure hiw they do it but I would imagine their is no switch at the detector dewelling unit.
I have combo smoke detrctor and carbon monoxide detector hard wired. Not sure hiw they do it but I would imagine their is no switch at the detector dewelling unit.
Sent from my SM-G935U using Tapatalk
The box is not the outlet. The outlet may be within the box. If all that is in the box is a simple switch, there is no outlet, that switch does not fit the NEC definition of outlet.
NEC said:Outlet. A point on the wiring system at which current is taken to supply utilization equipment.
If the electronics in the device is the utilization equipment, it can't also be its own outlet; it is powered from the outlet.If it is a complex switch, say a programmable switch or something, then the logic portion of the control will have an "outlet", IMO.
Not only the rooms mentioned, but the entire branch circuit must be protected. So if you install interconnected units all on one circu0
What if there is no gas burning appliances to create any CO?
A fireplace can generate CO2 also, as can a smouldering upholstery or carpet fire
Sent from my XT1585 using Tapatalk
Those events will trigger a standard smoke.
In Illinois, CO alarms are only required if the home is supplied with nat gas or has an attached garage.
Propane as well even if it’s just for those look nice fireplaces.
....I have combo smoke detector and carbon monoxide detector hard wired. Not sure how they do it but I would imagine their is no switch at the detector dewelling unit.
Sent from my SM-G935U using Tapatalk
I am just struggling with this might as well tell the story. Their was a job that I was doing brand new apartment complex almost height of high rise dewelling units brand new smoke detectors and inspector did not say anything and it was not on AFCI. Inspector said you never put smoke detector on AFCI. I looked all over for reason and IRC allows some household to have smoke detector fire alarm system but I am not sure if this job was one of them. I am not trying to troll but given the information on this and other threads it just looks odd and wanted your straight forward opinon thats all being that many dewelling units smoke detectors in height almost high rise. I noted the model number Universal Security part MIC1509S spec attached in Post #34 attachment. Is the inspector correct that it does not need AFCI? Thanks.
I am just struggling with this might as well tell the story. Their was a job that I was doing brand new apartment complex almost height of high rise dewelling units brand new smoke detectors and inspector did not say anything and it was not on AFCI. Inspector said you never put smoke detector on AFCI. I looked all over for reason and IRC allows some household to have smoke detector fire alarm system but I am not sure if this job was one of them. I am not trying to troll but given the information on this and other threads it just looks odd and wanted your straight forward opinon thats all being that many dewelling units smoke detectors in height almost high rise. I noted the model number Universal Security part MIC1509S spec attached in Post #34 attachment. Is the inspector correct that it does not need AFCI? Thanks.
Sent from my SM-G935U using Tapatalk
Inspector said you never put smoke detector on AFCI.
Iirc, that is the reason battery BU smokes became mandatory via nfpa
The irony being some states (such as mine) recently allowed for Lith-Ion (battery only) smoke installs
~RJ~
The inspector is correct. NO AFCI NEEDED.