ddservices
Member
- Location
- San Antonio,Texas,united states
I have a panel feeding a new bathroom addition. The home run is a 12/2 romex. feeding into a panel with a 3 wire feeder. So all the grounds and neutrals are landed on the same neutral bar. The installed breaker is functioning fine however my inspector is failing the job saying that the breaker will not function correctly due to the panel not having a dedicated ground in the feeder. But in my opinion this should not be an issue the breaker has no idea if the ground is separated or not. It is simply monitoring the return on the neutral and since this is a preexisting condition in a house over 40 years old it should not be cause for an inspection failure the new bathroom is wired to current code including the afci breaker. The home owner should not have to have their entire service and subpanel upgraded over 1 20 amp circuit. Looking for advice and if my line of thought makes sense.