I also initially understood it to be that way - even though not up to code (even at time of installation), that is typical when you do run into those situations.Methinks there's some confusion, the OP panel is an older 3 wire w/bond to it's shell
Most are.
I'm willing to bet the meter , if similar vintage , is also , the GEC could exist at either, depending on the poco
~RJ~
Biggest issue with it is potential voltage rise on EGC's and obejects bonded to EGC's, and/or neutral current being carried on those paths. If it were a subpanel feeding an entire second floor and there were no conductive paths to anywhere else - it sort of really doesn't matter if you ran three wires to said panel and then ran separate EGC's beyond that point. We do similar with services even when there is ground/grounded objects around.