dunriteman, I feel your pain. I too am in SC and know about having to use an AFCI on the smoke detector circuit just because it has a device attached within a bedroom, however you may be able to get your inspector to drop this requirement by citing the NEC (NFPA 70) 2005 (although the 2002 is the currently enforced version) section 760.21.
760.21 NPLFA Circuit Power Source Requirements.
The power source of nonpower-limited fire alarm circuits shall comply with Chapters 1 through 4, and the output voltage shall not be more than 600 volts, nominal. These circuits shall not be supplied through ground-fault circuit interrupters or arc-fault circuit interrupters.
FPN: See 210.8(A)(5), Exception No. 3, for receptacles in dwelling-unit unfinished basements that supply power for fire alarm systems.
The 210.8(A)(5) exception 3, just indicates that the circuit supplying the fire alarm panel cannot be considered the required circuit for the unfinished basement outlet(s) in exchange for not requiring GFCI and dedicating the circuit to the fire alarm panel.
May need to see if 760.21 is present in 2002 edition of NEC. Note that the AHJ may have an ammendment over-riding 760.21 as AFCI's are still a topic of contention in many localities.
Hope this helps.