Did find this
Neutral to ground detection starts about middle and goes most the way to the end of the article.
February 23 2018 By Lee Teschler said:
..The standard (UL 943) specifies that GFCIs trip with fault currents of 6 mA for specified ground fault resistances and for a specified combination of ground to neutral resistance and wire resistance between load/neutral and earth ground. In UL tests, the resistance of the combination of grounded and grounding conductors of the cable or cord are quite low, 0.4 and 1.6Ω at most.
Yes, I see Kwired reference it testable. Empirical evidence (Observation) appears to confirm Teschler's interpretation of UL 943 test requirements.
The problem is this can't be observed with typical testers in the field. While low-impedance solenoid testers are commonly used by Qualified Persons to trip a live GFCI when probed H-G, trying to probe N-G fails to trip in the same manner.
Qualified Persons may naturally assume, since their tools don't confirm it, the
Retro Encabulator's modial interaction of magneto reluctance and capacitive duractance, or some other BS is being sold by internet-trolling carpet baggers.
Qualified Persons wearing proper PPE would need to employ a shorting probe / wire across device N-G, since few solenoid testers, much less standard multi-meters are designed with internal impedance less than 1.6Ω, per Kwired reference to
Teschler and the UL 943 standard.
This is also noteable for most AFCI breakers observed with a similar function. N-G probes trip most AFCI's with high-impedance multi-meters, or just by placing Neutral and Grounding conductor in the same hand, with Hot capped off, and switch leg turned off. Wolfram Alpha lists the resistance of a typical human body as 2300Ω to 201kΩ with dry skin. If the UL 1699 standard for AFCI's has a similar test function to trip N-G, I'd guestimate the trigger-happy impedance would be somewhere in that range or higher.