i got one for a couple reasons.... i had a neutral fault test to pass,
and this made it easier to find the cross connect. as i posted earlier,
it'll detect a neutral / ground cross connect upstream for about 15'.
that'll let you test without loading the circuit. it's fast.
here's the other reason.... all the inspectors around here are starting to
get them. i don't call for inspection unless i know it'll pass, and if i don't
have the tool the inspector is gonna use, well, it's a crap shoot.
now, here's what i learned on here... dunno if it is out yet, but the newest
generation of suretest will tell the amount of load on a branch circuit, from
any point in the circuit.
so, if you are gonna buy one, check and see if the unit you buy has that
feature yet... mine doesn't......
it's also an excellent diagnostic tool on a number of levels. i had a 'pooter
network administrator having his undies in a wad about a power source
for his server.... i stuck the suretest on the outlet, and it comes up with
info that looks like this... it settles a lot of discussions.
first screen: all wiring correct, no cross connected neutrals / grounds
second screen: 121.2 volts rms h/n
0.1 volts rms n/g
171.3 volts h/n peak
60.0 hz frequency
third screen: voltage drop 4.4% @ 15 amps, 115.5 volts available
voltage drop 5.8% @ 20 amps, 113.9 volts available
voltage drop 3.5% @ 12 amps, 116.7 volts available
fourth screen: 480 amps bolted fault available at that point, h/n
550 amps bolted fault available at that point, h/n/g
fifth screen: .34 ohms total impedance, hot
.02 ohms total impedance, neutral
.25 ohms total impedance, ground
all of the values are from the point of connecton to the secondary winding
of the poco, or next upstream transformer.
sixth screen: gfci trips at 164 ms @ 7.4 ma
seventh screen: afci test... here is the instructions from the manual:
"AFCI breakers are prone to nuisance tripping when wired with a shared
neutral or when the neutral conductor is accidentally grounded before
the panel. The AFCI tripping occurs because it senses an imbalance
between the current going out on the hot and the current returning
on the neutral. A shared neutral between two hot conductors creates
this imbalance.
The SureTest can test for these conditions by applying a small load of 300mA
between hot and neutral to simulate a normal load and ensure that the AFCI
breaker does not trip. To conduct a shared neutral test, press the AFCI
button to enter the AFCI main menu. Press the side arrow ( ) to highlight the
NEUT symbol. Then, press the AFCI button to activate the test. The TEST
icon will light brightly while the test is being conducted. The AFCI breaker
should not trip. If the breaker does trip, a shared neutral is the probable
cause.