Would like opinions.

Would there be any benefit to installing arc fault protection to circuits that have knob and tube wiring that's still active?

Circuits originate as NM cable and are tied into knob and tube in ceiling boxes throughout the house.

Thanks
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
If permitted to keep the knob and tubing in accordance with 394, I would argue not in the defense of a benefit, but code requirements would determine if you should be using arc fault protection.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
We have done it because of the 6' distance issue. Occasionally all the K&T would need to be put on one breaker because of shared neutrals. Those installs usually were getting kitchen and laundry circuits added so most of the load was removed from the K&T.

Is there an advantage? Good question. Helps pass inspection? Maybe.
 