Meg the wireDennis Alwon said:Tried what?
Meg the wireDennis Alwon said:Tried what?
billsnuff said:Sidebar: Shared Neutral Applications
Single-pole AFCIs can't protect circuits in which the neutral (grounded circuit) conductor is shared or mixed because current flowing out and returning is monitored for the presence of arcing faults. When single-pole AFCIs are applied, the circuit must have a distinct hot and a distinct neutral conductor. Otherwise, the AFCI can't distinguish arcing ground-fault occurrences. General availability of a 2-pole AFCI should be expected at some point in the near future since the technology is readily capable.
Are you saying there is no kitchen in the whole building? If food is prepared in another building then I would say according to 210.12 you would not need arc faults. Seems odd but that's my read.craig65 said:I
There is a small kitchen, no stove, just microwave and sink , would you (anyone) consider this a dwelling unit? Does 210.18 apply?
there is a commercial kitchen at the back of the building that cooks all the meals for ther residents, they eat in the community dinning room.Dennis Alwon said:Are you saying there is no kitchen in the whole building? If food is prepared in another building then I would say according to 210.12 you would not need arc faults. Seems odd but that's my read.
Same is true for 210.8 (B) . If it's not a dwelling then no need however why wouldn't you have GFCI by the sink.
Just a note in 2008 Where receptacles are installed within 6' of a sink they must be GFCI protected in non- dwellings.
You may have some bad flashlights. I would try that first.
craig65 said:there is a commercial kitchen at the back of the building that cooks all the meals for ther residents, they eat in the community dinning room.
I asked the maint. man to unplug the flash lights ... it's worth a shot
All the sinks have GFIs.
I have a meeting with them tommorow afternoon,
we'll see how it goes...................
( to be continued)
I don't see why...this building does not meet the defintion of a dwelling unit and AFCIs are only required in dwelling units.Dennis Alwon said:If there is a kitchen in the building then I believe the arc faults are necessary.
don_resqcapt19 said:I don't see why...this building does not meet the defintion of a dwelling unit and AFCIs are only required in dwelling units.
no permenent cooking facilities only fridge and microacrwc10 said:Hum,,,behind the fridge, in the kitchen,, must need AFCI's then.....:grin: :grin: :grin:
craig65 said:found the problem... defective electrician. There was a j box behind the fridge with the neutrals were crossed.