arc fault

Status
Not open for further replies.
120 only yes, 120/240 MWBC no if it (the AFCI itself) has GFP.
What is the documentation for this? I don't understand why a circuit breaker based combination type AFCI that has ground fault sensing as part of its solution to the "Grand Concept of AFCI" can't function to protect either a single or multiwire ungrounded wiring method.
 
This:

http://apps.geindustrial.com/publib...lename=DET-719 CAFCI Shared Neutral Guide.pdf

I can't see why you can't do the same with a new BR AFCI (which I hear has no GFP)
O.K.

You must be saying, "Don't put a single pole combination type AFCI with GFP on one leg of a multiwire branch circuit."

I had assumed you meant a two pole combination type AFCI breaker. IMO, a two pole AFCI would work just fine on an ungrounded wiring method multiwire branch circuit, with or without the GFP component.
 
O.K.

You must be saying, "Don't put a single pole combination type AFCI with GFP on one leg of a multiwire branch circuit."

I had assumed you meant a two pole combination type AFCI breaker. IMO, a two pole AFCI would work just fine on an ungrounded wiring method multiwire branch circuit, with or without the GFP component.


But a two pole cost more $$$$$.
 