do the required outlets in the guest room (according to 210.60 a&b, refer to 210.52a ) require arc fault protection
Read 210.18 NEC 2005 or 2008scottysolar said:do the required outlets in the guest room (according to 210.60 a&b, refer to 210.52a ) require arc fault protection
scottysolar said:does 210.18 talk about guest rooms that do have provisions for cooking only. and does it talk about kitchen circuits not bedroom circuits
210.18 Guest Rooms and Guest Suites.
Guest rooms and guest suites that are provided with permanent provisions for cooking shall have branch circuits installed to meet the rules for dwelling units.
scottysolar said:210.52 deals with spacing requirements and the room must adhere to this
the sleeping area which is addressed in section#1 of 210 requires arc faulting ?
scottysolar said:210.52 deals with location of outlets not protectection .sleeping area protection is addressed in210.12.