Arc faults- Bedrooms and Smoke Detectors

Status
Not open for further replies.
Re: Arc faults- Bedrooms and Smoke Detectors

Originally posted by iwire:
George I am deeply hurt, far be it from me to stretch the NEC to my liking. :D :D

210.21(B)(3) Receptacle Ratings. Where connected to a branch circuit supplying two or more receptacles or outlets, receptacle ratings shall conform to the values listed in Table 210.21(B)(3), or where larger than 50 amperes, the receptacle rating shall not be less than the branch-circuit rating.
Seems as though this section is attempting to tell us the suitable receptacle ratings for the branch circuit values given. "The receptacle rating shall be this, the receptacle ratings shall conform..."

But I could be stretching this. :D

[ March 31, 2005, 10:13 PM: Message edited by: georgestolz ]
 