jcy123
 - Pittsburgh
 - Engineer
My company uses either Incident Energy Calculations or Arc Flash Category for PPE Selection.
The Incident Energy Calculation method for selecting appropriate PPE starts at 1.2 cal/cm^2. So far so good.
During a dead check of a piece of equipment, the incident energy was calculated to be 0.6 cal/cm^2 at the nominal working distance of 18" in SKM. The Arc Flash Distance is 12" per SKM.
A Fluke meter will be used with the normal leads in place. The technician will have on appropriate shock rated gloves and leather covers (Class 00, 480V). His hands, by nature of the equipment (just a box with some terminals inside) will cross the "Arc Flash Boundary" while doing the dead check.
What PPE is required to do the dead check on the equipment?