NEC/70E
NEC/70E
This is a very common misunderstanding. The only "installation requirement" is the generic arc flash hazard warning mandated in 110.16 which can be "field or factory marked."
Labeling of equipment with an incident energy (IE) level or an arc flash PPE category level is not an installation requirement. There is no requirement for any manufacturer or installer to apply such a label. There is no requirement that an inspector can cite to require such a label.
While the NEC and 70E both address electrical safety, they are dynamically different. The NEC (70) addresses installation requirements and 70E addresses electrical safe work practices. 70E cannot and does not contain any installation requirements. In fact, Chapter 3 of 70E was recently overhauled to remove many installation requirements.
The NEC and 70E are consensus documents. They can only become enforceable where they are adopted by a local municipality, city or state. The NEC is adopted in this manner but 70E is not.
There are many individuals that think 70E is an enforceable document because the style is similar to the NEC and it uses terms such as "shall or shall not." 70E is a standard, not a code. Read how NFPA defines those terms and you will see that a standard is designed to be adopted by other codes or referenced in regulations.
There are requirements that employers are legally bound to comply with but they are federal regulations as seen for example in OSHA 1926 and 1910. There are requirements in the OSHA standards that are reflected in 70E. In those cases, the reality is that OSHA is the shall, 70E just shows the employer how. It must be understood that 70E has requirements that OSHA does not, meaning there are no federal regulations that an employer must follow.
A close read of 130.5(D) in 70E 2015 reveals that after all of the parent text the last paragraph states that the installation, documentation and maintenance of the label is the responsibility of the owner of the electrical equipment. This text intentionally removes the installer from any such requirement. The bottom line is that labeling is optional and is at the whim of an owner. There is no federal regulation in OSHA 1926 or 1910 that requires labeling.
There are many blogs, articles and discussions about required labeling. It is all much ado about nothing because there is no requirement. It is simply an option of the owner.
There is a second revision in 110.16 for the 2017 NEC that requires labeling of service equipment rated 1200 amps or more. If it survives the process, the 2017 edition of the NEC will be the first to require such labeling and will be limited to services rated 1200 amps or more.