Thank you
I checked the link. Any suggestions where to go to figure out calculations for the degree of arc flash danger?
In the ceu it was mentioned how the degree is lessened as you go further from the source but that was all that was said about it. No I can't say that. They said you had to get the starting arc fault current from the utility company. They also mentioned that the utilities are installing larger transformers notifying landlords as by law they have to but not telling them that they need to be re calculated and possibly have all there equipment changed.
I went to a on line arc fault calculator but it's still a bit foreign to me.
Anything about calculating or posting arc fault in one or two family residence ( I guess except for the little red sticker of a guy getting blown up that you where supposed to stick on the cover that I haven't seen in years )
short of getting the current rating from the poco, there is little you can do
to calculate this. residential services, there is a smaller can feeding a number
of occupancies, usually. this cuts the Ka-Wham factor a lot.
a lot of stuff we run across in the general world doesn't have an arc flash sticker
on the panel. since i've been self employed, since 2005, i've yet to see one in any
situation, anywhere, there is a PPE sticker on the panel.
you look at what the POCO shows up wearing when they pull and set meters,
it's an approved face shield, and FR shirt, with 1KV gloves. a good starting point.
you should have that on your truck, period. good for about 7 calories or so.
i ended up needing a bunny suit, so my decision was based on what i'd been told
at arc flash class with LADWP... 40 calories is the practical limit of functionality,
as the blast from something bigger, the explosion will probably kill you. suits go
up to 100 calorie. they usually have blowers on the back to force air in, so you can
stand to work in them.
so, i bought a 40 calorie suit, and 15KV gloves, good for 40 calories. the gloves are
unsuitable for anything requiring manual dexterity. put a set of gloves and outers on,
and try to figure out which one is your thumb. but it's good for closing and opening
overcurrent. i'll use 1KV gloves if i need more dexterity.
is this approved means and methods? nope. but it's what i do personally. operating
without employees means i can apply common sense, if i have any. it's my ass i'm
directly affecting.
a full on 40 cal suit is about $1,500 or so.