NEC Require Arc-Flash Study?

NEC Require Arc-Flash Study?

Where in the NEC does it explicitly state that an arc-flash study must be performed? I know that 110.16 requires arc-flash hazard warning labeling, but doesn't require a study to be performed. Any insights?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
The NEC doesn't. OSHA states that all employers must provide a workplace that is safe from electrical hazards and must have a defined electrical safety program, SUGGESTING that it look like NFPA 70E.
 