That statement can be true for any piece of equipment with an arcing fault. An arcing fault can be very destructive with molten metal being airborne. So unless the piece of equipment is designed and tested as arc resistant, based on the statement above, an arc flash label should not be installed on any piece of equipment as one does not know what is going to happen.
Do you provide arc flash labels for equipment that is over-dutied? From what I gather, the consensus is to flag the equipment and provide suggestions for remedial action, possibly including upgrade or replacement of the affected equipment in order to comply with the NEC and NFPA 70E.