The NEC requires you to put a simple 'advisory' label on just about everything that could be serviced while energized.I am an Electrical Contractor.
When we install a new 480v breaker panel, are we required to install an Arc Flash Warning Label?
What if the panel is 208V??
What information needs to be included on this Label?
70E does have the 3 item exception (<240v, one supply and <125KVA). Keeping this in mind I do Not have to label <240v equipment at all.
NEC 110.16 does not specifiy voltages.
So are we to assume all voltages need to have a generic label per NEC?
Whick code are we to abide by??
Switchboards, panelboards, industrial control panels, meter socket enclosures and motor control centers that are in other than dwelling occupancies.........
Don't see voltage mentioned in there anywhere.
Don't think it's referred to there but calculating available levels of incident allows for choosing the correct PPE to be used by personnel, which is sometimes necessary per some OSHA regulations.
By the way, I'm a member of the local IEEE IAS (Industrial Applications Society) and at one of their meetings about two years ago they had a pretty heated talk about the merits of calculating based on 70E or IEEE1584. I would love to know what what some of you guys think about which is the superior method.
PPE and energy levels are required by NFPA 70E not the NEC, as far as OSHA is concerned the current "industry standards' are always in effect.We may be talking apple and oranges. We're still in the 2005 and you only had to have the arc flash warning lables stating that proper PPE must be worn. The lables that tell you about the zones are not required here yet.
I would think most companies that provide Arc Flash Analysis use software to do their calculations. I know ESA has software that is very user friendly and SKM is the most widely used. Does anybody know anything about either?
We may be talking apple and oranges. We're still in the 2005 and you only had to have the arc flash warning lables stating that proper PPE must be worn. The lables that tell you about the zones are not required here yet.
PPE and energy levels are required by NFPA 70E not the NEC, as far as OSHA is concerned the current "industry standards' are always in effect.
And how do you know what is "proper PPE" if the levels of incident energy are unknown?
I have no idea. I've been trying to get my bosses to send me to some classes, but with the budget cutbacks (training from $40K to $10K) I don't seem to really be getting anywhere.
Zog will usually jump in on a thread like this, I'm kind of surprised that we haven't heard from him.
There are no specifications for labels at all.Does NEC require an Arc Flash Hazard Label to be of any certain size?
Does NFPA 70E require a certain size?