(This is a new requirement with the 2008 code)
Arc Flash requirements started with the 2002 NEC.
(This is a new requirement with the 2008 code)
here we apply the label that states that if the dead front is removed while energized propper ppe will be worn.
I read about this a while ago and havent revisited the subject in a little while but if I remember correctly some people are advocates of using one PPE class above recommended because the PPE pretty much only means the operator will not suffer fatal injuries in the event of an arcing fault, but some pretty harsh damage can happen to the hands, arms and chest.
Arc Flash requirements started with the 2002 NEC.
Arc flash PPE is required when you are interacting with the equipment, operating a breaker for example, even with the covers on.
The PPE selected has to have an ATPV rating that is greater than the calulated EI. The ATPV is based on not allowing >1.2 cal/cm2 to pass through which is the 2nd degree burn threshhold. So with the right PPE selected burn injuries will be limited to a 1st degree burn.
The pressure from the arc is a different story, PPE gives limited protection from that part but there are not any usuable calculations (yet) to determine the pressures.