Arc flash labels for transformers
Isaiah
Baton Rouge
Electrical Inspector
The question came up today if power transformers 15kV to 480V require arc flash labels on both primary and secondary air terminal chambers - comments?
Enviado desde mi iPhone utilizando Tapatalk
Labeling is required for equipment likely to be serviced or examined while energized. A-F labels on transformers is common but not always done. If the two enclosures are physically separated, I'd put two labels. The alternative might be one label based on the higher of the two calculated incident energies.
.... based on the higher of the two calculated incident energies.
This is hard to justify. I would base a single label on the highest voltage and the source incident energy.
In a typical transformer, especially <150kVA, the HV and LV terminals are actually in between each other. You cannot have a fault involving one set of terminations without it propagating to the source side conductors. Of course this is not true for larger transformers and those with dedicated termination compartments.
You'd use the higher voltage and higher incident energy. I don't see much of an issue. I'm not sure what you mean by "source incident energy".
Usually the highest incident energy will be on the transformer secondary, primarily due to the impedance of the transformer lowering the available fault current.
My point is, you typically cannot create an arcing fault on the secondary terminals of most transformers without also creating an arcing fault on the primary terminals. If the primary terminals are involved in an arcing fault the transformer will effectively be removed from the circuit and therefore no longer contribute incident energy into the fault.