Arc flash labels for transformers

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
The question came up today if power transformers 15kV to 480V require arc flash labels on both primary and secondary air terminal chambers - comments?


Enviado desde mi iPhone utilizando Tapatalk
 
Labeling is required for equipment likely to be serviced or examined while energized. A-F labels on transformers is common but not always done. If the two enclosures are physically separated, I'd put two labels. The alternative might be one label based on the higher of the two calculated incident energies.
 
.... based on the higher of the two calculated incident energies.
This is hard to justify. I would base a single label on the highest voltage and the source incident energy.

In a typical transformer, especially <150kVA, the HV and LV terminals are actually in between each other. You cannot have a fault involving one set of terminations without it propagating to the source side conductors. Of course this is not true for larger transformers and those with dedicated termination compartments.
 