The right way to do it is to do the entire system, including the PV system, and run scenarios ranging from no Zero to 100% PV. If you're adding a 400 kW PV system, that'll contribute somewhere around 15 calories based on the numbers for a 400 kVA transformer, so that becomes significant. To Joethemechanic's point about maintenance folks not being trained from an arc flash standpoint, I say that varies greatly from plant to plant. I have experience with P&G, and I can say that they're programs are first rate and that all of their employees have PPE and wear it as appropriate. But the fact of the matter is that injuries from arc flash are few and far between, and 95% of electrical fatalities are from shock or contact with electricity. I think 70E goes to the extent it does to de-energize systems because that rare arc-flash injury can be so horrific. Take the Steve Lenz injury that was featured in the 2012 NFPA 70 (NEC) Handbook. He was hospitalized and had 5 skin peels before being released and all he was doing was installing a power monitor on the side of an 800-amp piece of gear, but a self-tapping screw pierced the insulation of a parallel 500 kCM conductor. It's those types of incidents that have driven 70E to be so seemingly paranoid. But as long as you wear PPE for the application, in accordance with table 130.5(C) Estimate of the Likelihood of Occurrence of an Arc Flash Incident, then you're covered.