pistolpigg
Member
- Location
- cookeville,tn
So just for argument's sake if you were to press a start button on an automatic starter disconnect combo you'd have to put a suit on if its arc flash analysis deemed it to have that incident energy?
So just for argument's sake if you were to press a start button on an automatic starter disconnect combo you'd have to put a suit on if its arc flash analysis deemed it to have that incident energy?
Or use a big stick to press the button lol. So even with that don't someone got to put ppe on to turn off so it can be locked out? Almost sounds like we need to come up with a means of remote lockout
Yes, you must wear the appropriate PPE to verify the absents of voltage as part of a lockout/tagout policy if you are within the arc flash boundary and the restricted approach boundary.
Chris
Absence of voltage does not have to be confirmed for all OSHA mandated LOTO procedures. For example, a local disconnect, between the starter and the motor, maybe Locked Out for changing a motor belt without ever 'opening' the disconnect enclosure.
But to operate that handle would you not have to have ppe ?Absence of voltage does not have to be confirmed for all OSHA mandated LOTO procedures. For example, a local disconnect, between the starter and the motor, maybe Locked Out for changing a motor belt without ever 'opening' the disconnect enclosure.
Now we are back to your company's Electrical Safe Work Practices requirements.But to operate that handle would you not have to have ppe ?
This is where the confusion lies and had made everything more complicated at most facilities all of them are more or less scared by the arc flash program and this fear of the worst case explosion at any interaction is causing most places to go with an overkill policy for the most mundane actions such as a mechanic or a production worker changing a belt or checking clearances is now requiring an electrician to operate a disconnect in the arc flash ppe.Now we are back to your company's Electrical Safe Work Practices requirements.
Your company needs to evaluate the risk once they know the 'worst case' outcome. As I have said before, NFPA70E purposely does not address this level of detail.
There is nothing in NFPA70E that would prohibit a non-electrician from becoming a qualified worker for a specific task.This is where the confusion lies and had made everything more complicated at most facilities all of them are more or less scared by the arc flash program and this fear of the worst case explosion at any interaction is causing most places to go with an overkill policy for the most mundane actions such as a mechanic or a production worker changing a belt or checking clearances is now requiring an electrician to operate a disconnect in the arc flash ppe.
There is nothing in NFPA70E that would prohibit a non-electrician from becoming a qualified worker for a specific task.
I agree that many people do not want any 'employee' judgment to be made concering NFPA70E required PPE. I wonder what they do about PPE for fall protection when working on a 10ft ladder in the middle of an office - where do they tie off? How about an extension ladder, how do they get to the top to secure it in place? When using cleaning products in the restrooms, are respirators always required or is risk considered?
I have also wondered why equipment is not required to contain the potential flash which would mean it is safe to operate a switch mounted on the enclosure? .
Simple answer, cost. There is a standard for arc rated enclosures and rated gear is becoming more common but it is a large cost adder. 10 years ago I did some testing on what was involved to retrofit old gear to meet the new standards and concluded is was not economically feasable to do so.
Would you agree that some older equipment maybe was better at protecting the operator? I have seen old panels that you about needed a crane to lift the dead front, but today an equivelant panel - one man can lift the cover without being a body builder. Much lighter gauge cans and covers in general today - mostly because of cost I assume.
I'm trying to figure out why and how it would logical to have to put a hrc four requirement to operate a disconnect for a motor when its load is disconnected by a motor starter or a drive. Seems like a lot of overkill for operating a device that has no load for example.