electricalperson said:
quick question. is HRC level 2 rated gear all thats needed for 480v 3 phase 3000 ampere switchgear? i plan on buying some ppe for myself soon and im wondering if level 2 gear is all thats needed. im also looking at level 3 but the website doesnt offer any level 3 kits. im not sure if level 4 is overkill or not. i dont want to minimize burning and injuries i dont want to be burned or injured at all in case of an arc flash/blast (if thats possible)
That may be a quick question but it is not a quick answer, the load has little to do with it. The factors are (simply put) available fault current and clearing time of the protective device.
With 3000A gear I will assume it is fed from a 2500 kVA transformer with about a 5% impedance which would give you about 60,000A of available fault current (Not accounting for any motor contribution). I will also assume the main breaker does not have INST protection, only ST, LT, and maybe ground fault.
The clearing time (At best ) will be 0.2 seconds which using the 70E equitions gives you 54.95 Cal/cm2 at 18", which is above the allowable level (Should be labeled "Dangerous") that the 70E lets you do any work. No PPE can protect you at that level, you could get a 1000 cal suit but it wont protect you from the pressures involved, but at least you can have an open casket.
480V switchgear is usually the worse case senario for arc flash, much worse than anything on the 13.8kV or 4160V part of the system.
P.S. All the numbers in my calcs are estimates and assumed values, but I think you get the idea.
Get some training before working on 480V switchgear!!!!!!!!!!!