Arc flash

Status
Not open for further replies.

j rae

Senior Member
Are you required to wear proctive gear if working on a 277v ballest if it's hot? What class would this be??
 
Are you required to wear proctive gear if working on a 277v ballest if it's hot?
Yes, you must always use the appropriate PPE. Per NFPA70E, I can find no reason you should be working on a lighting ballast "hot".
 
We have to fill out a hot permit and use class 1 safety ppe so we try to do it dead. We also wear fr clothing every day on the job 100% cotton. We treat 277 like 480 only because some electricians get caught between the neutral and we all no what that feels like (ouch)
 
Last edited:
after a guy got hurt from working on a ladder on 277 lighting it mad us think that yeh it`s only 277 but it can kill
 
Last edited:
Every light is fed from a circuit that is controlled by a switch. Just turn it off.
Your wife,children,parents,etc.. will be very happy to see you at the end of
your shift alive.
 
Are you required to wear proctive gear if working on a 277v ballest if it's hot? What class would this be??

NFPA 70E 2009

Other 600V Class (277V thru 600 V Equipment

Lighting or small power transformers

Work on energized conductors and circuit parts, including voltage testing.

HRC 2*

FR Clothing Min Arc Rating of 8

LS Shirt and Pant, Hard hat with Face shield and chin cup and balaclava,
rubber and leather gloves and leather shoes. Hearing protection and insulated tools.
 
20 cal shirt or jacket should be worn if working on hot just my 2 cents the above is correct it`s hard to believe someone can work with this ppe
 
Last edited:
Status
Not open for further replies.
Top