I don't believe that the _mounting screw_ is considered to provide an effective ground fault path for a self grounding device. I always thought that the little metal spring that holds the screw and gets wedged against the box was considered the required grounding connection. In this case, a plastic box extender would interrupt the connection.
However beyond this, I don't see using a plastic box extender as being any more or less permissible than using a plastic device cover plate, and something that may or may not be permissible depending upon circumstances. If the reason for using a metal box has to do with fire resistance, then IMHO iwire is correct, a plastic box extender won't do. But if the metal box is being used for other reasons, and fire resistance is not an additional requirement, then the plastic box extender might be just fine.
When using a metallic wiring method, at a minimum, you have to bond all of the metallic conduit or cable armor. This can be accomplished with plastic boxes with suitable bonding wiring, but a metallic box simply makes more sense. If the only reason for using the metal boxes was to provide bonding, then IMHO a plastic box extender would be sufficient.
-Jon
However beyond this, I don't see using a plastic box extender as being any more or less permissible than using a plastic device cover plate, and something that may or may not be permissible depending upon circumstances. If the reason for using a metal box has to do with fire resistance, then IMHO iwire is correct, a plastic box extender won't do. But if the metal box is being used for other reasons, and fire resistance is not an additional requirement, then the plastic box extender might be just fine.
When using a metallic wiring method, at a minimum, you have to bond all of the metallic conduit or cable armor. This can be accomplished with plastic boxes with suitable bonding wiring, but a metallic box simply makes more sense. If the only reason for using the metal boxes was to provide bonding, then IMHO a plastic box extender would be sufficient.
-Jon