weressl
Esteemed Member
Yes, this is from Mike Frain in the U.K.
"I've just had word back from Marchwood Power Station and it seems as though the incident actually occurred at a waste to heat site near Heathrow Airport, London. I'll try to follow this up after the Easter holidays to see if there is any further information available. The initial report came from an international contractor working at Marchwood on the commissioning of the station. The report said
"Just a reminder of what can happen if the PTW system is not followed correctly......This incident took place while the contractor asked for getting Breaker information. However; they did not take a work permit and tried to remove the breaker without permission that caused an electrical flash over. This incident gives us a lesson will be discussed and communicate with all of us to avoid such incident to occur.
EXECUTIVE SUMMARY
On 03/04/2009 at 08:40 hours an electrical flashover was reported while the contractor was trying to find the information regarding 480 KV breakers. This resulted in injuring three contractors employees; one with first degree burn and two with 2nd degree burns. All the victims were transported to clinic for first aid treatment and then transported to Care Hospital for further examination and treatment."
I'm still a bit confused as the 480kV probably means 480volts but this is not a standard voltage in the UK. The other issue is that information of an incident that is probably under investigation by the authorities does not appear so quickly in the public domain here. It is however a solemn reminder of what can go wrong on an ordinary piece of low voltage equipment. Mike "
I have another source working on this investigation, no info from him yet that he can discuss but i will post that when I get it.
Interesting, all the equipment seem to be ANSI. Could our house-Britts
Especially since it is the old ITE gear that Siemens taken over in the US and only marketed it in the ANSI region since they have their own EC gear and now in the US they sell that Furnas $^&%*$ and the ITE gear is obsolete.