Is it tripping on fault or current? What's the amp reading tell you? Test it under load. Have you megged the device and circuit?I am having trouble with a square d arch fault breaker tripping when my customer runs on her treadmill. It is a dedicated 20 amp circuit and it tripps after running 5 to 10 minutes.I have tried another breaker. Any ideas?
My circuit breaker keeps tripping too. I wonder if you could help me trouble-shoot it? Here I am using the vacuum right before the breaker tripped:equipment like this seems to be a problem with these breakers I see it with vacuum cleaners.
	This question has come up before on this forum I believe or that may have been a GFCI, but it was a treadmill.
It does not dump to ground unless there is a fault. If that were the case all of our generators would just dump to ground. It goes back into the feeder and pushes power to another point on the grid. If another load does not use it, and it does not go back to the motor, it will be dissipated by the grid.I remember it was a GFI circuit. I questioned then how a treadmill dumps surges on the EGC. One instant, the motor is under load and acting as a motor. The next instant, the motor is unloaded, oversped, and becomes a generator,all thaat happens in a split second, and repeatedly. Where does this surge go? What does the treadmill do with this generated energy? I be;live it dumps it onto the EGC. Thus tripping AFCI's and GFI's . But I'm only guessing, there could be something wrong with the treadmill. Check ground path back to service panel.
Isn't Ohio land of the Hoover?lol!! thats funny
I know what my answer has been to nuisance tripping AFCI's :grin:
Could it be something with the fact that treadmills use PWM DC motors?Here was another such discussion:
http://forums.mikeholt.com/showpost.php?p=1130922&postcount=13
There seem to be plenty of posts regarding problems with arc fault breakers tripping on certain types of loads. I am sure lots of the trips are "real" problems that need to be addressed.
I also believe that AFCI's are not perfected yet and that they do often nuisance trip under the right conditions. Some manufacturers designs are probably better than others.
I have been waiting and hoping to hear from someone with an issue like this who has installed an EMI filter inline with the load to see if that helps or not.
Arc Fault breakers are sensitive to higher frequencies to assist in detecting an arc. The EMI filter could possibly help filter those higher frequencies before they can reach the breaker. It would need to be a good quality EMI filter that has a larger inductive component (a good attenuation figure at the lower frequencies).