120v 20 amps...read the section but wondered if there was a "fixed equipment" type of exception but I don't see one.
Do Cadet heaters installed in wall in a bedroom of a new house need to be on arch faults?
sounds like I need them! but if i fed them
from 240v i wouldn't?
You are correct Sir. Fortunately for us VA does not not enforce 210.12 from the 2008 NEC, only 2005 NEC. At least that's what I've been told from the jurisdictions we work in.
So what do you do when you are doing replacements under the 2012 or whatever the new code is.
Considering the fixed in place Cadet Baseboard heater, from the OP, the "outlet" is splice in the wiring compartment on one end, or the other, of the heater.Code specifies "outlets". Outlet is sometimes an ambiguous term. Our jurisdiction terms lights as outlets, haven't had the debate on fixed in place equipment. Probably required. I'll ask the question next time I have a consult with a local inspector.
The wirenut connection of the branch circuit conductor to the heater's internal conductor is the "outlet". (Remember, the Article 100 Definition says: "A point on the wiring system . . . ") Saying it another way: The Cadet equipment conductors connect to the building branch circuit conductors at the Outlet.
If the heater is supplied by a 120 volt 15 or 20 amp branch circuit, and the heater is in the areas described in 210.12, then 210.12 applies to it and an AFCI OCPD must be installed.
Give them (the Code Making Panels, and the writers of Proposals) a few more code cycles and we'll probably go there. Initially, the new-fangled AFCI, that was slow to get to market, had a very limited area that it had to protect. The area of AFCI protection has been steadily expanding since 1999. First it was only "receptacle outlets" which are defined in Article 100. Then it was changed to "outlets", the general term, to include "lighting outlets", smoke detectors, etc.Then why does 210.12 use the term. 120-volt? Why not say any outlet regardless of the voltage?