TwoBlocked
Senior Member
- Location
- Bradford County, PA
- Occupation
- Industrial Electrician
I have seen conductors ground out and blow fuses due to vibration in rigid conduit installed in class I div 2 areas. As per code, the conduit is not sealed because the entire run is within the classified area, and terminates in enclosures with devices acceptable in CID2 areas. When examining the damaged conductors, it is obvious that significant arcing takes place. Of course if in the middle of a conduit run there was, by design, open contacts that spark when opening or closing, conduit seals would be required. And of course the grounding fault is NOT by design. Yet it could still be expected. (And occurs often enough to BE expected). Forgive me for not going into more detail. I have pics I don't feel I am at liberty to post.
Soooo .... , I will be involved in installing conduit and wire in a similar situation. Doing so is acceptable and expected, but I don't feel good about it. Am considering pushing for sealing these conduit runs. If I do, I expect there to be push back because if (when) the same fault occurs, there will be a much longer period of down time to repair the fault. another option is to install some sort of hardened cable, instead of ordinary conductors.
Oh, there will not be detailed specs given that need to be followed.
Comments?
Soooo .... , I will be involved in installing conduit and wire in a similar situation. Doing so is acceptable and expected, but I don't feel good about it. Am considering pushing for sealing these conduit runs. If I do, I expect there to be push back because if (when) the same fault occurs, there will be a much longer period of down time to repair the fault. another option is to install some sort of hardened cable, instead of ordinary conductors.
Oh, there will not be detailed specs given that need to be followed.
Comments?