hi every one I'm an apprentice and had an install where we had a feed through lug kit (ftlk) energize a tesla back up gate way and had no ocpd except the main breaker and i don't think that's correct i was always told never go lug to lug and read 240. 21 and looked into buss way taps and taps in general and saw that its okay for the tap not to have ocpd but once it reaches it device it's supplying it should land on a breaker of some sort unless there's a fused disco in between and also i may be completely wrong because i don't even know what a (ftlk) is even classified as i will appreciate any guidance on this because I'm verry con fused
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It is not a tap if the OCPD ahead of the feed-thru lugs is not larger than the conductors you install in the feed-thru lugs.
 
Location
ca
Occupation
solar
so if i have a 200 amp breaker and 3/0 awg conductors coming out of the lug kit to the switch gear it isnt a tap, but im still confused on what the (ftlk) is and in that scenario the main breaker is okay to be the ocpd for that switch gear
 
Location
ca
Occupation
solar
and to make sure i understand when you say the ocpd ahead of the (ftlk) is not larger the the conductors we are talking about ampicity wright
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
so if i have a 200 amp breaker and 3/0 awg conductors coming out of the lug kit to the switch gear it isnt a tap, but im still confused on what the (ftlk) is and in that scenario the main breaker is okay to be the ocpd for that switch gear
It's basically a continuation of the buses in the panel.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
and to make sure i understand when you say the ocpd ahead of the (ftlk) is not larger the the conductors we are talking about ampicity wright
Yes if you had a 200 amp main with lugs attached to the bottom of the bus you can run 200 amp conductors without an additional OCPD because they are already protected by the main.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Here's a photo that may help. 400 amp main in first panel to 400 amp bus in second panel with 400 amp conductors.
Copy cat!
rofl1.gif
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I think that we posted at the same time. And BTW you stole my photo! :giggle:
Actually, I found it on the net and posted it first, but your copy is clearer, so I replaced it with yours.

So we can certainly say that your post helped to clarify mine. ;)
 