Doing an arc flash study. The utility services the site with 34.5KV, and they step it down to 4160V with an on-site substation.
I got the following info. from the utility:
I'm trying to figure out which numbers to plug into SKM, and trying to make sure all the numbers make sense. On the 34.5KV side, I converted the thevenin impedance numbers to per unit numbers using:
Zpu = Z/Z base
and;
Zbase = Vbase^2/MVA base
Then I entered the 34.5 KV short circuit currents, and the Per unit Z's were close to my calculated numbers (close, but not exact). Like this:
But then I tried the same thing on the 4160 V side by making a 4160V utility source. At the lower voltage, the thevenin impedances don't seem to match the fault currents. I tried going back and forth, and even using a different voltage as the base voltage, but nothing seems to match.
Did the utility make a mistake on the numbers they provided, or am I doing something wrong?
The fault currents at the 34.5KV Tap are as follows:
3LG = 15475A
2LG = 7908A
LG = 10474A
LL = 13400A
34.5KV BUS
THEVENIN IMPEDANCE (OHM)
Z(+) = 0.17454+j1.30862 Z(-) = 0.17506+j1.30891 Z(0) = 0.75464+j3.12885
Fault currents at the 4.36KV Tap are as follows:
3LG = 6761A
2LG = 7018A
LG = 6887A
LL = 5855A
4.36KV BUS
Z(+ ) = 0.00787+j0.38293 Z(-) = 0.00788+j0.38293 Z(0) = 0.00507+j0.36191
Zpu = Z/Z base
and;