The biggest problem with IG systems is constantly demonstrated on this site, a misunderstanding of how to install the system.
In my expierence if an electrical distribution system is properly installed, IG is of no benefit. If a distribution system is not properly installed and there are PQ issues related to this, IG should not be installed the wiring issues should be corrected.
We (the industry as a whole) would be better served if ALL electricians understood how to install a basic electrical distribution system, free of shorts and free of accidental or intentional ground connections that are inappropriate.
I have seen many IG systems installed and few if any are properly installed, the electricians can't get the basic electrical system installed properly, they sure as heck are not going to install a system with extra grounding requirements installed properly.
Cross connections between IG and "normal" EGC.
IG taken to separate isolated electrode.
IG circuits normal outlets.
NO IG circuits IG outlets.
IG and EGC tied together at the outlet.
IG ground ISOLATED (no connection to anything)
Total isolation (ungrounded system)
Total isolation no EGC, PVC coupling in EMT run to 3 phase 3-wire computer on isolators and unit tied to separate ground electrode (lighting had fun with this isolation).
More rods driven than Cabela's has sold in a decade drive to correct PQ "issues".
And various HOODOO VOODOO the electricians DODO, in attempts to resolve grounding requirements and PQ issues.