winnie
Senior Member
- Location
- Springfield, MA, USA
- Occupation
- Electric motor research
An extremely common practice is to use the 'add the kVA' to size the loads on individual busses in a 3 phase panel.
So for any 3 phase load you take the total load kVA, divide by 3, and assign that value to each bus.
For a single phase L-L load, you take the load kVA, divide by 2, and assign that value to each connected bus.
For a single phase L-N load, you take the load kVA and assign it to the connected 'hot' bus.
Question are there any corner cases where this would result in an underestimate of the individual phase load?
So for any 3 phase load you take the total load kVA, divide by 3, and assign that value to each bus.
For a single phase L-L load, you take the load kVA, divide by 2, and assign that value to each connected bus.
For a single phase L-N load, you take the load kVA and assign it to the connected 'hot' bus.
Question are there any corner cases where this would result in an underestimate of the individual phase load?