Hello jimbom7859.
The general answer to your Q is no. They are approved for a voltage, and amperage, certain wire sizes, and other such stuff like this, and not based on the land use zoning of a facility. But there are certain applications in an industrial environment that they are not permitted. You should review the NFPA 79, "Electrical Standard for Industrial Machinery". If you are going to use them in light fixtures, or receptacles they are likely fine. But, the NFPA 79 has certain applications that would disallow the use of these. For example, 13.1.2.1 "Conductors and Cable Runs" states: "Conductors and cables shall be run from terminal to terminal without splices or joints." This would exclude the use of any type wire splice. Also, Ch 13 "Wiring Practices" 13.1.1.8 states "Means of retaining conductor strands shall be provided when terminating conductors at devices or terminals that are not equipped with this facility. Solder shall not be used for that purpose". This is generally interpreted to mean that you need to install wire end terminals (boot laces) unless the terminal has that little square plate with the terminal screw in the center. It seems not feasible to use a boot lace in these WAGO devices.
As for motor terminations, section 13.5.9.2 "Motor Connection Boxes" states "Electrical connections at motor terminal boxes shall be made with an identified method of connection. Twist-on wire connectors shall not be used for this purpose". 13.5.9.3 states "Connectors shall be insulated with a material that will not support combustion". You will need to determine the fire insulative properties of the WAGOs and whether or not they satisfy the identified method of connection.
Hope this helps rather than make the Q more confusing...