Area
Good evening...would you be so kind and explain the following. I cannot find the table where the area of wire is indicated. In the basic electrical theory DVD.
16AWG Stranded
Area 1,620 CM
Diameter 0.015 in.
R. 8 ohms per 1,000 ft.
I have looked in table 5. :? is there One for stranded and One for solid?..:dunce: Thank You
ggunn
Austin, TX, USA
16AWG Stranded
Area 1,620 CM
Diameter 0.015 in.
Make sure you are using the correct area in your calculation. If resistance is what you are calculating/comparing (for example, the necessary adjustment of an EGC size when you increase the size of the current carrying conductors), use Table 8; this gives you the cross sectional area of the metal in the conductor. If it is conduit fill you are working on, you need to use Table 5 (which refers to the specific wire type) because it's the total area of the metal and the insulation that is pertinent.