The NEC requires that calculations be made using their motor amps no matter what the actual motor amps are for most motors. However, they do not cover motors for voltages over 2300V and there are also some other configurations not covered. In order to calculate the required breaker, disconnect and conductor sizing, does one default to the manufacturer's full load current?
The NEC allows for the conductors to be smaller in motor sizing than what would be required for other loads based on the breaker size. Do I have to size the conductors for the breaker sizes for motors that are not covered in the amperage charts in section 430? This would obviously require conduit and wire very much larger than what is required using the full load amps from the charts in lieu of sizing them by the size of the protection.
For motors the breakers can be 800% vs. the normal 125%, and the wires just have to be 125% of FLA.
The NEC allows for the conductors to be smaller in motor sizing than what would be required for other loads based on the breaker size. Do I have to size the conductors for the breaker sizes for motors that are not covered in the amperage charts in section 430? This would obviously require conduit and wire very much larger than what is required using the full load amps from the charts in lieu of sizing them by the size of the protection.
For motors the breakers can be 800% vs. the normal 125%, and the wires just have to be 125% of FLA.