mikehughes8
Senior Member
- Location
- NC
I have a few questions regarding direct buried armored cable.
320.108 Equipment Grounding Conductor.
Type AC cable shall provide an adequate path for fault current as required by 250.4(A)(5) or (B)(4) to act as an equipment grounding conductor.
How does one determine whether or not AC cable make an adequate EGC. Does it have an equivalent wire size?
250.84 Underground Service Cable or Raceway.
(A) Underground Service Cable. The sheath or armor of a continuous underground metal-sheathed or armored service cable system that is connected to the grounded system conductor on the supply side shall not be required to be connected to the grounded system conductor at the building or structure. The sheath or armor shall be permitted to be insulated from the interior metal raceway or piping.
If a utility XFMR is feeding a Main Distribution Panel that in turn feeds sub-panels on different buildings am I correct that under this code reference I would connect the armor at the utility and omit that connection at the service equipment? Or do I have to maintain continuity up to the sub-panels on each building?
If I am not allowed to omit this connection wouldn't I be creating a parallel path back to the source using the armor and the grounded conductor?
310.7 Direct-Burial Conductors.
The metallic shield, sheath, or armor shall be connected to a grounding electrode conductor, grounding busbar, or a grounding electrode.
In all other cases the armor is required to be connected to a ground bus etc. If it does not meet the requirements of an EGC IAW Art 250.4 a supplemental EGC must be utilized. Is this a correct assessment?
320.108 Equipment Grounding Conductor.
Type AC cable shall provide an adequate path for fault current as required by 250.4(A)(5) or (B)(4) to act as an equipment grounding conductor.
How does one determine whether or not AC cable make an adequate EGC. Does it have an equivalent wire size?
250.84 Underground Service Cable or Raceway.
(A) Underground Service Cable. The sheath or armor of a continuous underground metal-sheathed or armored service cable system that is connected to the grounded system conductor on the supply side shall not be required to be connected to the grounded system conductor at the building or structure. The sheath or armor shall be permitted to be insulated from the interior metal raceway or piping.
If a utility XFMR is feeding a Main Distribution Panel that in turn feeds sub-panels on different buildings am I correct that under this code reference I would connect the armor at the utility and omit that connection at the service equipment? Or do I have to maintain continuity up to the sub-panels on each building?
If I am not allowed to omit this connection wouldn't I be creating a parallel path back to the source using the armor and the grounded conductor?
310.7 Direct-Burial Conductors.
The metallic shield, sheath, or armor shall be connected to a grounding electrode conductor, grounding busbar, or a grounding electrode.
In all other cases the armor is required to be connected to a ground bus etc. If it does not meet the requirements of an EGC IAW Art 250.4 a supplemental EGC must be utilized. Is this a correct assessment?