Last couple days my co worker posted a question in regards to 223.30. we established running one feeder to a building was the only way. this project
was asked of us last year and but hadn't got it yet. Today we arrive onsite to find out our customer already had someone else do work. they apparently
did exactly what we were gonna do if they had 3 separate Temporary Buildings. unfortunately its one big building.
lucky for me after spending all weekend asking questions and research on this site. I knew they were in violation. 223.30. the owner asked me to fix the
work utilizing all the available materials if I can.
The service now is feed from exisiting 800a service its about 150' away from temporary building. the T building needs 600A to feed 3- 200am MCB panels inside
Temporary buildings. they installed 3 -200a disconnects at 2nd h frame they hung on H frame because they weren't allowed to hang panels on side of temporary building. the H frame sites about 15' from side of Temporary Buildings.
My Idea is to use the overhead as parallel out of Service gutter to a 600a disconnect on 2nd H frame then feed all the 200a disconnects going to 200MCB goin in the building. Anyone see where this couldn't work. BTW there's no inspections its in the county.
was asked of us last year and but hadn't got it yet. Today we arrive onsite to find out our customer already had someone else do work. they apparently
did exactly what we were gonna do if they had 3 separate Temporary Buildings. unfortunately its one big building.
lucky for me after spending all weekend asking questions and research on this site. I knew they were in violation. 223.30. the owner asked me to fix the
work utilizing all the available materials if I can.
The service now is feed from exisiting 800a service its about 150' away from temporary building. the T building needs 600A to feed 3- 200am MCB panels inside
Temporary buildings. they installed 3 -200a disconnects at 2nd h frame they hung on H frame because they weren't allowed to hang panels on side of temporary building. the H frame sites about 15' from side of Temporary Buildings.
My Idea is to use the overhead as parallel out of Service gutter to a 600a disconnect on 2nd H frame then feed all the 200a disconnects going to 200MCB goin in the building. Anyone see where this couldn't work. BTW there's no inspections its in the county.