You can mix & match wire sizes as much as you want. Just protect the entire circuit based on the lowest ampacity conductor.
I've installed lot lighting (480V) on 2-pole 20a breakers. I run #12 from the breaker to the contactor, then run something substantially larger such as 6 or 4 out to the pole bases. #10s get run up each pole. As long as the breaker protects the 'weakest link', life is good as far as the NEC is concerned.:wink:
I agree with what the others have said.
As 480sparky pointed out, it is common to upsize wire for voltage drop. This is fine provided that the OCPD is sized to protect the smallest conductor.
Chris
When I was inspecting for a company years ago, if I encountered the situation where the circuit would originate in #12 and have #14 downstream, I would ask the electrician to tag the wire in the panel to indicate not to protect at more than 15 amps. Never had a problem with that.![]()
When I was inspecting for a company years ago, if I encountered the situation where the circuit would originate in #12 and have #14 downstream, I would ask the electrician to tag the wire in the panel to indicate not to protect at more than 15 amps. Never had a problem with that.![]()
As long as you just suggested it and not required it I would be fine with it.
Chris
That's all I would do. And I would also explain that he did not have to since it was not required by code. In this way I was able to have cooperation with no problems. You get more bees with honey than you do with vinegar. :smile: