Art. 250 - Corner Grounded Delta

Status
Not open for further replies.

bigapple

Member
Does Article 250 permit a solid corner ground on a 480 Volt Delta secondary transformer winding? In this application a 750kVA, 208V Delta to 480V Delta step-up transformer is used in a high-rise commercial office building. Its purpose is to step up the system voltage to more efficiently carry power a long distance up the high-rise building, where it is then stepped back down through a 480V Delta to 208Y/120 step-down transformer. I'm having difficulty determining whether such an application is code compliant. Should the 480V system be grounded, ungrounded or impedance grounded? All opinions are welcome. Thanks.
 
Re: Art. 250 - Corner Grounded Delta

There is no code requirement that this system be grounded. This system can be ungrounded, soldily grounded or impedance grounded. It is a design choice. See 250.20(B), 250.21(4) & (5), and 250.36.
Don
 
Re: Art. 250 - Corner Grounded Delta

Don is correct, but it makes me wonder why the service isn't 480 delta to start with?
 
Re: Art. 250 - Corner Grounded Delta

Originally posted by dereckbc:
Don is correct, but it makes me wonder why the service isn't 480 delta to start with?
This building is in Manhattan, where the service voltage is dictated by the utility (Con Edison). In some areas of Manhattan Con Ed only provides 208Y/120V. It is not unusual to see large 208-480V step-up transformers specified when buildings undergo electrical renovations. Typically, however, the transformers are 208 Delta to 480Y/277V and the 480V secondary is solidly grounded.
 